phild Posted December 6, 2004 Report Share Posted December 6, 2004 Hello Does anyone know of how to change the analogue output through the menu to be used as motor current reading to a PLC from a CET4.From what I have read 100 % equals 12 mA.I have had a look through the setup and can't see the parameter to enable or disable. There are three possibilities. Analog output motor currentAnalog output therm. utilisationAnalog output PT 100 temperature.Somewhere in the manual probably will be the answer, so hopefully someone may have had the pleasure. regards Phild Link to comment Share on other sites More sharing options...
GGOSS Posted December 8, 2004 Report Share Posted December 8, 2004 Hello phild, Don't waste your time going through the manual. Unfortunately, the analogue output on the CET4 is not scaleable. The fact that you know 12mA = 100% should allow to scale the PLC accordingly. Hope the above helps. Regards,GGOSS Link to comment Share on other sites More sharing options...