Jump to content

Star Delta CB trip on delta


Guest Anonymous

Recommended Posts

Have had a Star Delta Starter in situ for a number of years...It now trips the CB when changing over to delta... do you think that this is due posibly because as the motor gets older (the enviroment is chlorine also) the synchronous speed or 90% is not reached in star before the delta change over and as such upon change over the extra transients are now tripping the CB. I personnally would like to change it to soft starter, but i need to justify the change over costs....etc... ;d;
Link to comment
Share on other sites

If it was working fine and nothing else was changed, I think your hypothesis has merit. Open Transition Y-Delta spikes can be very high and dangerous to other equipment in your entire facility. The worst effect comes from the motor slowing down slightly during transition, allowing the Delta connection to be made after the motor has lost momentum. That coupled with the inherent phase shift that occurrs going from Y to Delta, and you have the motor windings being out of phase with the line. As your motor got older, the bearings and other mechanical components in the load are wearing, so it may require just a bit more starting torque. This increases that momentum loss and the transition spike gets worse rapidly.
"He's not dead, he's just pinin' for the fjords!"
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×