Hi there, i need some input from you guys. I have this Siemens VFD installed in our plant. It drives a 11kw motor to rotate a Drum/cylinder. All of the time when i stopped it, the VFD gives an alarm of phase loss. I tried to measure the voltage while stopping but the voltage is present at all phase. I have tried to adjust the ramp down time but no success is obtained... Hope you can help me on this.. TNX
Link to comment
Share on other sites

Hi

 

I have come across this type of performance if the inertia of the drum is too high, or is unbalanced.

I would try to set the ramp down period to a long setting, or to set the stop mode to coast down.

 

Best regards,