Guest Posted January 21, 2005 Report Share Posted January 21, 2005 Hi, kWHr is a part of kVAHr. How can there be no change in kVAHr when there will be change in kWHr, since the PF at Meter end remain constant? If capacitor bank has to reduce its load, what would be the impact on saving? Thanks. Link to comment Share on other sites More sharing options...
marke Posted January 22, 2005 Report Share Posted January 22, 2005 It is certainly possible to change the KVAHr without changing the KWHr. If you have a load with a lagging power factor and add power factor correction, the KWHr will remain unchanged, but the KVAHr will fall. The power factor will also improve. If you have a motor with a smal load, the change in load will affect the KWHr but have very little impact on the KVAHr. The KVA is the vector sum of the resistive power and the reactive power. If the reactive power is significantly larger than the resistive power, small changes in the resistive power (KW) will not show up in the KVAHr. Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
Guest Posted July 12, 2005 Report Share Posted July 12, 2005 we often come to see that power supplying companies donot send the power at improved power factor to the domestic consumers .is it not feasible to improve the power factor ? or it is not economical Link to comment Share on other sites More sharing options...
marke Posted July 12, 2005 Report Share Posted July 12, 2005 The power supply companies do not supply power with a poor power factor. Power factor refers to the ratio between the KW and KVA drawn by the consumer. It is not related to the supplier.Domestic loading is primarly resistive and electronic. There is very little inductive load in the domestic situation so there is no advantage in power factor correction. There is however, a reasonable amount of electronic load which contributes to distortion power factor. It is best to keep quiet about this as we do not want the power companies to add a surcharge for harmonics!! Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now