marke Posted April 26, 2005 Report Share Posted April 26, 2005 Here is a simple solution for using the FDU on single pump irrigation systems with a pipe fill operation and a sleep mode operation. Operational Parametersparameter : function : Suggested start point500 : Running Pressure : Dependent on transducer321B : Pipe Fill Speed : 30 - 35 Hz822 : Pipe Fill Pressure : About 10-20% running pressure321A : Minimum speed : Set to keep pumping (30-40Hz)322A : Maximum speed : 50Hz28F : Sleep frequency : Equal to or greater than min speed (321A)28G : Sleep Delay : 30 seconds28H : Wakeup pressure : 50-90% of running pressure ConnectionsLink : #10 to #20Start : #8 to #11Pressure Transducer : #3 (-ve) to #11 (+ve) Setup in this order: 212 = keyboard 213 = remote 214 = R 281 = ON 282 = 2 287 = 0% 288 = 98% 28F = 30Hz 28G = 30 seconds 28H = 30% 28I = Fall 441 = !A1 821 = ANIN2 822 = 10% 234 = A 311 = 10S 315 = 10S 321A = 30Hz 322A = 50Hz 343A = ON 416 = 4-20mA; Set link S$ on pcb to current 234 = B 321B = 30Hz 322B = 50Hz 343B = Invert 234 = Digin3 Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...