taknavaz Posted October 13, 2005 Report Share Posted October 13, 2005 hellowhat is the formula for calculation the time of the timer for star- delta motors?thanks. Link to comment Share on other sites More sharing options...
marke Posted October 13, 2005 Report Share Posted October 13, 2005 Hello taknavaz While it is possible to calculate the time in star for a star delta starter, it is easier to use trial and error.To calculate, you need to know the speed torque curve of the motor in star and the speed torque curve of the load, plus the inertia and full speed of the driven load.To set empirically:Set the time longer than you expect, and measure the time taken for the motor to reach full speed. This is the timer setting you require.If the motor can not reach full speed due to insufficient torque, then the timing is not so relevant as the motor will draw almost locked rotor current after switching to delta. The best setting is to change over when the motor ceases to accelerate and further. Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
bob Posted October 14, 2005 Report Share Posted October 14, 2005 Hi Marke , I have come across two interesting phenomenons in start-delta applications. We had on site a 55 k W 400 V motor driving a fan. This motor took around 20 seconds to reach full speed in star position. This motor burned for some reasons and a similar motor !!! 55 k W 400 V was used to replace the burned on. The new one was never able to reach full speed in star position and obviously pumped the LRC on switching to delta. Basically, the characteristic of this motor is such that it could not develop the required torque in star position to reach the full speed of the load. Regards. Bob Link to comment Share on other sites More sharing options...
marke Posted October 14, 2005 Report Share Posted October 14, 2005 Hi Bob,Yes that is a common occurance. There are major variations between motors that are the same size.Why did the first motor fail?? was it a rotor failure or a stator failure?If it was a rotor failure, it could indicate that the rotor was not suitable for the inertia of the load, or that the starter remained in star for too long. Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now