smiki Posted November 12, 2005 Report Share Posted November 12, 2005 Hello,How can I define size of the contactor for star delta switch.I have motor on the sit for 250 Kw I=465A.I there any different in star and in delta. Link to comment Share on other sites More sharing options...
jraef Posted November 13, 2005 Report Share Posted November 13, 2005 The main run contactor must be sized for a minimum of 58% of the motor power, so in your case, 145kW or more. The other motor contactor needs only be rated for the remaining 42%, so in this case 105kW, but check with your preferred vendor to see if a mechanical interlock works with disimilar contactors, not all manufacturers do. If not, use the same size as the main. The star contactor needs to only be rated for 33%, so 83kW. "He's not dead, he's just pinin' for the fjords!" Link to comment Share on other sites More sharing options...
GGOSS Posted November 15, 2005 Report Share Posted November 15, 2005 Hello Smiki, I am firm believer that all electical equipment should be selected on the basis of motor nameplate Full Load Current and not just kW. Based on that I would suggest the following. Line Contactor: 270 Amps AC3Delta Contactor: 270 Amps AC3Star Point Contactor: 154 Amps AC3 Make sure that you use a dedicated star/delta timer ie a dedicated star/delta timer includes a inbuilt delay to ensure that the Star Point Contactor has de-energised and the arc has been fully extinguished before the Delta Contactor is energised. A standard timer does not provide this functionality and if used can result in the Delta contactor closing on a short and welding. jraef, I am interested in your ptroposal of having a motor contactor with a 42% rating. Could you please explain that for us. Regards,GGOSS Link to comment Share on other sites More sharing options...
jraef Posted November 16, 2005 Report Share Posted November 16, 2005 58% through the main "delta" contactor, 42% through the other one = 100%Take a look at this drawing. In that configuration (sorry, US nomenclature), the 1M contactor is sized for 58%, but the 2M contactor needs only be sized for the remaining 42% technically. http://www.ssusa.cc/reference/wiring_diagrams/standard_series_drawings/series_107/107_21.pdf I was incorrect about the mechanical interlock however, that needs to go between 2M and S, not 1M and 2M, so it will almost always involve dissimilar contactor frame sizes. I was trying to o from memory, which is frequently faulty. OK, I have edited this several times and can't get the BB code to ork right, so cut and paste into a browser window. Sorry. "He's not dead, he's just pinin' for the fjords!" Link to comment Share on other sites More sharing options...
marke Posted November 16, 2005 Report Share Posted November 16, 2005 Hello jraef Surely the current through the main contactor and the delta contactor are equal? both are carrying winding current so should be rated at 58% of the line current?Star delta starters are foreign to the USA so we have to make allowances!! Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
Guest Posted November 16, 2005 Report Share Posted November 16, 2005 Let me put these in formulae and be more specific. With reference to Jraef's circuit: 1. Isolator must be at least rated for motor line current In=465A. 2. Star contactor S (first to energize)must be at least rated for motor line current divided by 3 or In/3 = 465/3 =155A. 3. Main contactor 1M (energizes after S)rated for motor line current divided by square root of 3 i.e. In/1.73=270A 4. Delta contactor 2M (third to energize, S off)rated for motor line current divided by square root of 3 i.e. In/1.73=270A 5. Overload OLrated for motor line current divided by square root of 3 i.e. In/1.73=270A 6. type of contactor AC3: applicable for starting and stopping squirrel-cage motors Link to comment Share on other sites More sharing options...
msdaif Posted November 16, 2005 Report Share Posted November 16, 2005 Originally posted by AnonymousLet me put these in formulae and be more specific. With reference to Jraef's circuit: 1. Isolator must be at least rated for motor line current In=465A. 2. Star contactor S (first to energize)must be at least rated for motor line current divided by 3 or In/3 = 465/3 =155A. 3. Main contactor 1M (energizes after S)rated for motor line current divided by square root of 3 i.e. In/1.73=270A 4. Delta contactor 2M (third to energize, S off)rated for motor line current divided by square root of 3 i.e. In/1.73=270A 5. Overload OLrated for motor line current divided by square root of 3 i.e. In/1.73=270A 6. type of contactor AC3: applicable for starting and stopping squirrel-cage motors Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now