SAMER Posted November 28, 2005 Report Share Posted November 28, 2005 hiin fact i have two question:1)for a small evaporator 3 phase star/delta connection, to keep maximum air flow we connect the motor as star or delta? 2)when you close main duct dumper to reduce C.F.M for DX units, evaporator motor ampere will increase, decrease or no change? Link to comment Share on other sites More sharing options...
johnbose Posted November 28, 2005 Report Share Posted November 28, 2005 Depending on the inertia of the Fan, it may be difficult to start the motor in delta as starting currents can remain high for longer times. The manufacturer / supplier must have envisaged normal operation in delta, . MAx CFM is expected in delta.For any fan with damper in duct, closing of damper will reduce the load on the fan and thus the motor Link to comment Share on other sites More sharing options...
GGOSS Posted November 29, 2005 Report Share Posted November 29, 2005 Great reply johnbose. Both accurate and to the point. Keep up the good work. Regards,GGOSS Link to comment Share on other sites More sharing options...
petronila Posted December 1, 2005 Report Share Posted December 1, 2005 hello Sammer, About your first question: If you have a D/Y Three Phase Motor this motor could be connected at both voltages, then you have to use the right connection for the main voltage. Example: 220/400 Volts the 220 Connection is DELTA and the 400 V is Star.Refer to the name plate. Regards Petronila Link to comment Share on other sites More sharing options...
SAMER Posted December 4, 2005 Author Report Share Posted December 4, 2005 HI Johnbose I think when you close the damper to reduce the CFM that's mean there is obstacle resist the air flow this cause more difficulty for the motor to pass the air that's mean load increase on the motor so current should be increased.What's your opinion? Link to comment Share on other sites More sharing options...
GGOSS Posted December 5, 2005 Report Share Posted December 5, 2005 Hello Samer, When the damper is closed there is no movement of air and therefore there is no load. Regards,GGOSS Link to comment Share on other sites More sharing options...