chaterpilar Posted November 30, 2005 Report Share Posted November 30, 2005 Why is that all electrical panels come with control voltage transformers. Say a panel has 380 V 3 phase incomer...then 2 phases are taken into a 380v to 220 v transformer, and this voltage is used in control circuits. What is the advantage of this system? Can we put a 13.8 kv/ 220/110 volts dyn11 transformer and use 220 volts supply ( phase to phase ) for control voltage in 33/13.8kv substations? chaterpilar Link to comment Share on other sites More sharing options...
johnbose Posted December 2, 2005 Report Share Posted December 2, 2005 Control transformers are provided mainly for following reasons1. To have isolation from the Main supply2. To limit fault levels in control ciruit3. To have a safer and lower control voltage As far as second part of the question is concerned if u are planning to take secondary of the MAin transformer it msy not be a good idea ( Sl No 2 above ) It is also a good practice to use secondary centre tap earthed control transformers so that those working on the system are subjected to a lesser voltage w.r.t ground Link to comment Share on other sites More sharing options...