chaterpilar Posted December 24, 2005 Report Share Posted December 24, 2005 Is it neccessary to put a contactor on the output of VSD ? The freewheeling effect of motor gives feedback to VSD , especially if the VSD is driving a 2 pole pole motor and is stopped but motor keeps running..due to inertia. chaterpilar Link to comment Share on other sites More sharing options...
marke Posted December 25, 2005 Report Share Posted December 25, 2005 Hello Chaterpillar Generally, you would not put a contactor on the output of a VSD. Most VSDs will be damaged if you control a contactor on their output. and so it must not be done. There are some manufacturers who claim that you can use a contactor on the output of their drives, but this is not normal. Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...