emike Posted November 17, 2006 Report Share Posted November 17, 2006 i AM TRYING TO FIGURE OUT HOW TO CALCULATE FOR A MAIN DISCONNECT FOR A CONTROL PANEL. THE PANEL CONSISTS OF A VARIETY OF VFD'S RANGING FROM 1 HP TO 15 HP @ 480 VOLT. CAN ANYONE HELP ME OUT? THANKS Link to comment Share on other sites More sharing options...
jraef Posted November 17, 2006 Report Share Posted November 17, 2006 Read the Max. Amps on the nameplates of all the VFDs, add them together, mutiply the sum by 1.25 and pick the next size main breaker available. "He's not dead, he's just pinin' for the fjords!" Link to comment Share on other sites More sharing options...
jOmega Posted November 20, 2006 Report Share Posted November 20, 2006 Following JRAEF's advice, it is important to remember that when adding up the currents of all the VFD's .... that you use the listing for the INPUT AMPS and not the output amps. They will be different numbers because of the POWER FACTOR of each VFD. jΩ Link to comment Share on other sites More sharing options...